    Water Cooling Spreadsheet




    * Spreadsheet *
    Water Cooling Estimator


    ************************************************** *************************

    ************************************************** *************************
    Last update Download

    http://www.coolingtechnique.com/down...andrea-22.html



    Spreadsheet * Comparative analysis of the Fans tested by Martin Liquid Lab
    Air trough radiator ? Swiftech MCR120

    Last update Download


    http://www.coolingtechnique.com/download/cat_view/84-programmi-di-calcolo-per-lair-cooling.html

    ************************************************** *************************


  2.   Sponsored Advertisements
      Guest
    To Remove Ads... Please   Login or Register  
  3. #2
    Senior CTzen
    Data Registrazione
    Dec 2008
    Messaggi
    715
    Thanked: 0

    RE: Water Cooling Spreadsheet *

    Istruzioni per usare il foglio elettronico
    (LAST UPDATE : 01 2010)

    Descrizione dei vari fogli:
    Interface------Flow Rate----Rad RPM>TEMP----RAD RPM>WATT----RAD WATT>TEMP
    WB__C°/W > Flow Rate ---- WB in Sys A and WB in Sys B.


    ************************************************** *************************
    Interface :

    Configura il System A e il System B.



    Inserire manualmente (digitare) :
    temperatura ambiente C°
    Watt RAD. = Watt assorbiti dal radiatore = calore dissipato (in Watt)
    coeff.*Watt CPU = Watt assorbiti dal Water Block (Watt CPU) moltiplicato per un coefficiente
    caratteristico di ogni sistema determinato da diversi parametri ad es: resistenza termica della pasta termica (Tim C°/W) , dal sistema di misurazione della temperatura (sensori main board) ecc.



    Per calcolare i watt assorbiti dal radiatore (watt CPU + Watt GPU + ca 50 watt per pompa e mainboard):

    http://www.extreme.outervision.com/tools.jsp#cpuoc
    http://extreme.outervision.com/psucalculatorlite.jsp
    http://web.aanet.com.au/SnooP/psucalc.php

    ************************************************** *************************

    Selezionare i vari componenti del sistema A e B (due sistemi per poterli confrontare immediatamente):



    ************************************************** *************************

    Selezionare il tipo di ventola e la velocitį di rotazione RPM (menu)
    PUSH PULL ( ON OFF ) .........
    se si seleziona ON Il foglio calcola come se fosse presente il doppio di ventole che lavorano in push pull.




    ************************************************** *************************

    Selezionare le unitį di misura (menu) per pressione portata e lunghezza (per i tubi)




    ************************************************** *************************

    Il foglio di calcolo indica :

    Flow rate del sistema A e B.
    Differenza Temp. tra temperatura acqua e temperatura ambiente.
    Differenza Temp. tra temperatura Core CPU e temperatura acqua.
    Temp. CPU (temperatura core CPU).



    ************************************************** *************************

    Flow Rate

    (Quantitį di acqua che attraversa il circuito nell'unitį di tempo.
    LPH = litri per ora LPM = litri per minuto GPM (USA) = galloni per minuto.)
    Il grafico descrive l'andamento del flow rate del sistema A e B:



    Il flow rate del sistema č dato dal punto di intesezione tra la curva dell'efficienza della pompa
    e la curva della resistenza idraulica dei componenti selezionati (sistema A e sistema B)
    ************************************************** *************************

    RAD RPM>TEMP

    Il grafico descrive l'andamento della differenza tra temperatura acqua e la temperatura ambiemte
    (ossia la temperatura dell'aria che entra nel radiatore) in funzione dei RPM delle ventole.
    In pratica rappresenta l'efficienza del radiatore.



    Se in un sistema vengono selezionati 2 radiatori il foglio di calcolo considera e indica
    l'efficienza della somma dei 2 radiatori.



    ************************************************** *************************
    RAD RPM>WATT

    Il grafico descrive l'andamento dei watt dissipati dal radiatore
    mantenendo fissa a 1° C la differenza tra temperatura acqua e la temperatura ambiente
    al variare dei RPM delle ventole.
    NB : i watt sono direttamente proporzionali a questa differenza quindi dovendo dissipare
    una quantititį di watt 5 volte superiore avremo una differenza tra temperatura acqua e
    la temperatura ambiente 5 volte superiore.



    ************************************************** *************************

    RAD WATT > TEMP

    Il grafico descrive l'andamento della differenza tra temperatura acqua e la temperatura ambiente
    in funzione dei dei watt dissipati dal radiatore.
    Un altro modo per rappresentare l'efficienza del radiatore.



    ************************************************** *************************

    WB__C°/W > Flow rate > Temp

    Il grafico descrive l'andamento della resisteza termica (C°/W) del WB selezionato
    nel sistema A e nel sistema B in funzione del flow rate.



    ************************************************** *************************

    WB in Sys A: and WB in Sys B:

    Il grafico da una panoramica della differenza tra temperatura CPU e temperatura acqua
    di tutti i WB presenti nel foglio di calcolo.
    Una comparazione tra tutti i WB che lavorano nelle medesime condizioni;
    alimentati tutti dalla stessa pompa , selezionata nel sistema A e sistema B.
    Il modo corretto per confrontare le prestazini dei WB.







    ************************************************** *************************
    Data source :

    MLL = Martin's Liquid Lab data
    http://martin.skinneelabs.com/
    Cpu block Marked (MLL) = Martin's Liquid Lab
    - Intel Core Q6600 @3600 1,47V

    HES = HESmelaugh
    http://www.dexgo.com/index.php?site=...ardware&id=378
    Cpu block Marked (HES) = HESmelaugh
    http://www.xtremesystems.org/forums/...d.php?t=224976
    - Intel Core i7 920 @ 3.7GHz, 1.28V

    Cpu block Marked (**) = Other sources from the Web
    - Intel Core i7

    ************************************************** *************************


  4. #3
    Senior CTzen
    Data Registrazione
    Dec 2008
    Messaggi
    715
    Thanked: 0

    RE: Water Cooling Spreadsheet *

    ************************************************** *************************

    Radiators with fans in push pull

    See:
    Mathematical extrapolation of the data on the efficiency of radiators.
    http://www.xtremesystems.org/forums/...0&postcount=18


    Consider the structure of 2 radiators identical.
    The surface of the radiators and the number of the fans different .

    Mathematical formula for radiators (same structure):
    C°/W A = thermal resistance of the radiator with 3 fans ........ height of surface rad.A= hA
    C°/W B = thermal resistance of the radiator with 2 fans .........height of surface rad.B= hB
    formula:
    C°/W B = C°/W A*(((3fans/2fans)+(hA/hB))/2) = C°W A*(((2/3)+(hA/hB))/2)
    C°/W A = C°/W B*(((2fans/3fans)+(hB/hB))/2) = C°W B*(((3/2)+(hB/hA))/2)

    Analogously ..............

    Push Pull .........

    The structure of 2 radiators : identical
    The surface of the radiators : identical
    The number of the fans = X*2

    Mathematical formula for radiators (same structure):
    C°/W A = thermal resistance of the radiator with X*2 fans ....... height of surface = h
    C°/W B = thermal resistance of the radiator with X fans .........height of surface = h

    formula:

    C°/W A = C°/W B*(((Xfans/X*2fans) + (h/h))/2)
    = C°/W B*((( 1/2) + (1))/2)
    = C°/W B*(0.5+1)/2
    = C°/W B*0,75

    C°/W A = C°/W B*0,75


    Push Pull in the Spreadsheet


    ************************************************** *************************

    Another example of validity of extrapolation of the data:

    Fans in push pull mode .......

    This is a chart published by Martin



    I indicated the two temperatures interesting.

    Radiators with fans in push pull

    formula:

    C°/W A = C°/W B*0,75

    ....... 10,1° * 0,75 = 7,575°........very similar to the data published by Martin.

    ************************************************** *************************

    Update :
    Formula Push Pull improved .... more precise.........


    The old formula considered (Push Pull = Fans x 2)
    http://www.xtremesystems.org/forums/...19&postcount=6
    The new formula considers (Push Pull = CFM x2)
    It is mathematically more complicated.
    Example:
    This is the equation of the radiator Thermochil pa 120.3 :
    Temp.=8,31*RPM^-0,86
    This is the equation of the radiator Thermochil pa 120.3 Push Pull :
    Temp.=8,31*(1,4142^-0,86)*RPM^-0,86.

    practically....
    With the old formula:
    temp push pull = 0,75 temp no push pull
    With the new formula:
    temp push pull = 0,742242981 temp no push pull
    In this case the difference among the two formulas is least.
    With other radiators he can be great.

    ************************************************** *************************


  5. #4
    Senior CTzen
    Data Registrazione
    Dec 2008
    Messaggi
    715
    Thanked: 0

    RE: Water Cooling Spreadsheet *

    ************************************************** *************************
    change the fans
    Thanks to the study of Martin.
    http://www.xtremesystems.org/forums/...d.php?t=223391
    It is possible to change the fans....


    ************************************************** *************************
    Transformation Skinnee Lab Fans in Gentle Typhoon Fans

    Skinnee Lab Fans data:


    RPM Ultra kaze 3000 > RPM Gentle Typhoon AP 15 :



    RPM Yate Loon D12S H > RPM Gentle Typhoon AP 15 :



    RPM Yate Loon D12S L > RPM Gentle Typhoon AP 15 :



    Substitution of the RPMs and new equation :


    ************************************************** *************************

    Likewise : Gentle Typhoon > Nanoxia FX 2000


    ************************************************** *************************


  6. #5
    Administrator L'avatar di Damiano
    Data Registrazione
    Apr 2008
    Localitą
    Uboldo (VA)
    Messaggi
    19,868
    Thanked: 611

    RE: Water Cooling Spreadsheet

    Fatto
    Precedente discussione:
    http://www.coolingtechnique.com/forum/showthread.php?tid=269&page=2
    Download Spreadsheet da coolingtechnique.com:
    http://www.coolingtechnique.com/download/doc_details/29-water-cooling-spreadsheet-by-andrea-22.html

    Rinnovo i complimenti per l'ottimo lavoro nonchč dedizione.

    PS:abbiamo risolto pił bug stasera che in 4 mesi di utilizzo


  7. #6
    Senior CTzen
    Data Registrazione
    Dec 2008
    Messaggi
    715
    Thanked: 0

    RE: Water Cooling Spreadsheet

    Spreadsheet V. 2.00 2009!!
    Sono stati inclusi tutti i WB testati da Martin
    ......... And more
    Download in the first page! (post)


  8. #7
    Staff CT L'avatar di Oreste
    Data Registrazione
    Apr 2008
    Localitą
    Vienna
    Messaggi
    9,142
    Thanked: 4

    RE: Water Cooling Spreadsheet

    Io aspetto 3 giorni e poi lo vedo con calma,che qui sono a CB sul portatile con openoffice (prima che lo scarico office...ač)


  9. #8
    Staff CT L'avatar di Oreste
    Data Registrazione
    Apr 2008
    Localitą
    Vienna
    Messaggi
    9,142
    Thanked: 4

    RE: Water Cooling Spreadsheet

    Curiosando,leggendo velocemente le review di vkbms (volevo capire da quanto tempo utilizzava i suoi strumenti), sono capitato sulla review dell'EK...

    http://www.nexthardware.com/recensioni/scheda/71_486.htm

    noti qualcosa di strano?


  10. #9
    Senior CTzen
    Data Registrazione
    Dec 2008
    Messaggi
    715
    Thanked: 0

    RE: Water Cooling Spreadsheet

    Citazione Originariamente Scritto da Snowfortrick
    Curiosando,leggendo velocemente le review di vkbms (volevo capire da quanto tempo utilizzava i suoi strumenti), sono capitato sulla review dell'EK...

    http://www.nexthardware.com/recensioni/scheda/71_486.htm

    noti qualcosa di strano?

    A quei tempi usava strumenti scarsotti vedi fluximetro.
    (per questo ti ho chiesto che fluximetro ti propone)
    La piattaforma HW era diversa.Q 6600 ecc.
    ........... questi dati non sono stati inseriti nello Spreadsheet.
    Oltre a questo .... che hai notato di strano?
    I dati new sul EK li ha successivamente pubblicati assieme a quelli dei new WB in un quadro comparativo ..............

    http://www.nexthardware.com/recensioni/scheda/119_951.htm

    http://www.nexthardware.com/recensioni/scheda/111_855.htm

    sono i dati next che ho inserito nello spredsheet.


  11. #10
    Staff CT L'avatar di Oreste
    Data Registrazione
    Apr 2008
    Localitą
    Vienna
    Messaggi
    9,142
    Thanked: 4

    RE: Water Cooling Spreadsheet

    no io avrņ il flussimetro serio,il key instrument,prima usava tutt'altro come hai potuto vedere.Io pensavo che nel foglio ci fossero quei dati,evidentemente allora vkbms ha ritestato l'ek con la piattaforma seria,quindi ho solo fatto confusione io

    ps:ho ordinato anche la pompa



Discussioni Simili

  1. Componenti nuovo impianto water cooling
    Di Wanderlust nel forum Configurazioni e worklog
    Risposte: 38
    Ultimo Messaggio: 15-09-2014, 09:17 PM
  2. i7 3770k e water cooling:questo sconosciuto....Help Me
    Di dax4you nel forum Configurazioni e worklog
    Risposte: 9
    Ultimo Messaggio: 24-12-2012, 01:13 PM
  3. HAF 932 Full Water Cooling
    Di Black_Out nel forum Configurazioni e worklog
    Risposte: 40
    Ultimo Messaggio: 20-01-2012, 04:32 PM
  4. Swiftech H20-220 Apex Ultima Water-Cooling Kit Review
    Di Redazione nel forum Comunicati stampa dai partner
    Risposte: 0
    Ultimo Messaggio: 16-01-2009, 04:35 PM
  5. Water Cooling Spreadsheet
    Di Andrea 22 nel forum Liquid cooling generale
    Risposte: 27
    Ultimo Messaggio: 03-01-2009, 11:12 PM